Hi Dewar:
Pizzafanatic is correct, the code does not care about extracting heat just cooking vapors, That type eye brow hood does not extract heat from the top ,front or back a lot of heat remains in the kitchen.
We designed and sold a 100’s of those type hoods back when the regulations were simple.
Today that type hood would be required to exhaust 3000 cubic feet of air per minute. It would need ether an 18 or 20 ton air conditioner Or a 3000 cfm make up air unit to compensate for the air being pulled out of the building. If A/C were used you would be throwing out 3000 cfm of expensive cooled air per minute.
If you used a makeup air unit it would cost about $4,000.00 to $5,000 to install and another $4,000.00 per year to operate depending on your location. Also during the summer a make up air unit would be pumping 3000 cfm of very hot air off your roof into your building requiring more A/C to compensate for that heat.
The hood we have that was specifically designed to overcome the problems outlined above extracts The maximum amount of heat from all around the ovens but only takes 720, 800 or 880 cfm of air from the building depending on oven size. This system costs about the same as the Eye brow hood used with a make up air unit or with a larger A/C system. But it costs thousands less than ether of those systems in yearly operating costs. Reason: our system does not have to heat or cool any air.
Paul points out that the eye brow hoods will not work efficiently on triple decks. He is correct the cfm of the exhaust system has to be cranked up so high to capture from the bottom deck that all the heat is usually pulled out of the top oven and often the bottom one is not sufficiently captured.
Additional notes the eye brow hoods work the same and require the same exhaust and make up air be the ovens gas or electric.
Also note kitchen vent elation is not required by code to address heat in the kitchen it is required by code just to extract the cooking vapors. Cheep vent elation systems meet the code but do not take out much heat and usually require a vast amounts of make up air.
If not done properly the ventilation system can leave your kitchen uncomfortably hot and cost thousands per year to operate.
George Mills